I can't speak for all utilities on this.
Around here though the additional fuse above is aggravating to install, but during a storm they are extremely beneficial.
A CSP has a weak link primary fuse that can't be replaced in the field.- this means during a lightning storm (most are during bad lightning) the internal fuse may blow and it requires a changeout.
Sometimes the internal secondary breaker goes out, again, requiring a changeout. Linemen break the breakers slamming the handle up and down. They think the harder you slam it the better chance it will stay in..
With a conventional transformer it's lighter, all the protection is outside the tank, and easier to replace a blown fuse.
With that being said, we have had a tap with 7 transformers on it and the mainline fuse was blown, along with 4 other fuses above conventional transformers. A man in a pickup can replace the fuses and get everyone back on. No need for a bucket truck that's busy changing a CSP transformer.
It's a total ownership cost issue, and maintenance has to be taken into account.
I don’t climb or get in the bucket anymore, but in the 90s early 2000s I've changed many CSP damaged by lightning. Never changed a single conventional transformer from lightning.
One issue here though..
Say you have a small mill that's about 45kW load.
So we build a bank and fuse the bank for (generally) twice the bank output.
We have had instances where a motor got locked up and blew fuses in the mills. Electrician or maintenance man comes to fix it and ups the fuse, or worse yet sticks a piece of copper pipe in there. The motor locks up, and blows out primary fuse.
Some of the linemen that won’t call me have been known to put a bigger fuse in to stop it from blowing.
Fuse too high on the primary and the transformers gonna blow before long.