rick hart
Senior Member
- Location
- Dallas Texas
I need some help sorting through this:
Four 100HP constant volume condensing water pump motors are tripping overloads. Motors are getting hot and trip in the hottest part of the day and randomly at night. Not good to lose AC in a Texas summer. Measurements at the motor show average current above the namplate and a voltage unbalance of approx 1% at each motor and a current unbalance of approx 8-12% on C phase. This voltage unbalance can be traced back to the service entrance. So far so good, I found the problem with the overheating and overload. Not!
The utility says they are allowed 3% UNLOADED at the meter. We are loaded to over 4.5 MW so I don't know what to make of this. The phase angle is good and right where it should be ( 0, 120, 240) but, the magnatude of A-B deviatrion from average is right at 1%, give or take a tenth depending on the time of day.
Most of what I can read about the issue says 1% is all NEMA will go for at the motor and the only thing I can find that says otherwise is a single IEEE whitepaper stating that, "Oh, 2-3% is not that big a deal" and a buch of calculus to demonstrate the opinion. The majority of resources says more than 1% reduces effeciency and heats the motor, including our Department of Energy. The motors are hot and overloaded -1% sounds like all I want to accept.
I know there are quite a few utility guys out there. What voltage unbalance are you allowed to get away with?
Also, what can I look for on my side that might be the cause? My current is about 4 amps out per phase max on a 222A average demand (13.2kV service) on two separate feeders, one has problems the other does not.
Thanks
Rick
Four 100HP constant volume condensing water pump motors are tripping overloads. Motors are getting hot and trip in the hottest part of the day and randomly at night. Not good to lose AC in a Texas summer. Measurements at the motor show average current above the namplate and a voltage unbalance of approx 1% at each motor and a current unbalance of approx 8-12% on C phase. This voltage unbalance can be traced back to the service entrance. So far so good, I found the problem with the overheating and overload. Not!
The utility says they are allowed 3% UNLOADED at the meter. We are loaded to over 4.5 MW so I don't know what to make of this. The phase angle is good and right where it should be ( 0, 120, 240) but, the magnatude of A-B deviatrion from average is right at 1%, give or take a tenth depending on the time of day.
Most of what I can read about the issue says 1% is all NEMA will go for at the motor and the only thing I can find that says otherwise is a single IEEE whitepaper stating that, "Oh, 2-3% is not that big a deal" and a buch of calculus to demonstrate the opinion. The majority of resources says more than 1% reduces effeciency and heats the motor, including our Department of Energy. The motors are hot and overloaded -1% sounds like all I want to accept.
I know there are quite a few utility guys out there. What voltage unbalance are you allowed to get away with?
Also, what can I look for on my side that might be the cause? My current is about 4 amps out per phase max on a 222A average demand (13.2kV service) on two separate feeders, one has problems the other does not.
Thanks
Rick