I have a job 120/240 v high leg delta. there are 4 panels, only 1 is 3 phase for air conditioning. The 3 panels are 1 phase 120/240 v, drawing under 200 a each. The 4th panel is 120/240 delta with a high leg ( B at panel ) with a 88 amp draw on the B phase. The other phases, A & C, draw around 200 A each. There are only 2 circuits, 1 A-N & 1 C-N
presently being used at about 10 A each. most of the loads are 1 phase 240 v ac's connected between A & C phase. Can I move some of the single phase ac's to A-B & B-C
which would give me more available current to work with on my A & C legs ? The neutral is full size to the panel. The high leg coming in from the utility company has only 88 amp load at present and is extremely under loaded, as it is 500 mcm when it could be reduced down to 4/0 safely..
Thanx, dhsvcs
presently being used at about 10 A each. most of the loads are 1 phase 240 v ac's connected between A & C phase. Can I move some of the single phase ac's to A-B & B-C
which would give me more available current to work with on my A & C legs ? The neutral is full size to the panel. The high leg coming in from the utility company has only 88 amp load at present and is extremely under loaded, as it is 500 mcm when it could be reduced down to 4/0 safely..
Thanx, dhsvcs