I have a situation where a hospital wants to install UV-C lights in a wet procedure room on all 4 walls. According to NEC Article 410.10(A), all luminaires installed in wet locations shall be marked "suitable for wet locations".
NEC definition of a wet procedure location is "the area in a patient care space where a procedure in performed that is normally subject to wet conditions while patients are present, including standing fluids on the floor or drenching of the work area, either of which condition is intimate to the patient or staff".
Would Article 410.10(A) be applicable whereas the UV-C light fixtures need to be marked "suitable for wet locations"? According to Article 410.10(A) and the wet procedure room definition it appears that they do. Any thoughts would be appreciated. Thank you.
NEC definition of a wet procedure location is "the area in a patient care space where a procedure in performed that is normally subject to wet conditions while patients are present, including standing fluids on the floor or drenching of the work area, either of which condition is intimate to the patient or staff".