V.D of Elevator feeder, total 290 feet away

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi ,
in a certain situation , because of relocation of existing service,
i have to re feed the existing 3-phase elevator;
existing elev. feeder is 90 feet thru 3/0 CU.

Can I provide new 200ft 4/0 Cu from the new service location , and connect to the existing 90- feet . 3/0 CU thru a right-size pull box ??????????

Thank you
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Without addressing the size of the conductor(s) needed, in principal there is no reason you can't have a feeder with one portion using a larger conductor than a second portion as long as the smaller cable is protected at its ampacity,.
You would need to take 250.122(B) into account.
 