V-drop Calc verification and other such inquiries

Status
Not open for further replies.

sparkydon

Member
Hello fellow folks of the electrical world, glad to stumble upon this site...this is my first post so bear with me...

I am currently working on a project (residential) that has been my most challenging up to date. A 2600 sqft. home is being built a top a ridge where the utility main service is located 390ft. from my loadcenter in the house. The service is rated at 200A and PG&E (utility company) brought the service as close as their engineerng would permit. From the main, I am feeding 180ft to a generator/pumphouse to an external subpanel and then the final 210ft. to the house's subpanel. There will be zero deviation in the trenching. Basically from point A-B-C.
I Propose to bring the entirety of the Ampacity of the main to the pumphouse (200A), and then supply the house with 150A of ampacity..When I did the calculations, I came up with 250MCM CU THHN would carry 150A for 390ft. @ an allowable 2.99% voltage drop...

My questions are:
-Is that conductor size appropriate for the desired ampacity/length of run?

-Is there a more economical and code compliant way to achieve these specs (parallelled aluminum conductors etc..)

-Should I be concerned with the fact that the utility maxxed out their service distance to begin with??

Thanks in advance for any input...
Don
 