the maximum volt ampere loading permitted on a 20 ampere branch circuit with a continuous load would be
20x120x1.25 percent=3000va. Correct?
20x120x1.25 percent=3000va. Correct?
the maximum volt ampere loading permitted on a 20 ampere branch circuit with a continuous load would be
20x120x1.25 percent=3000va. Correct?
No.
20x120/1.25=1,920 va
Alternatively, 80% of 2400VA (20x120) also equals 1,920VA. Division by 125% (5/4ths) is the same as multiplication by 80% (4/5ths).
Of course it is, but the OP and the NEC reference 125% so that is what I chose to show for clarity.
210.20 Overcurrent Protection. Branch-circuit conductors
and equipment shall be protected by overcurrent protective
devices that have a rating or setting that complies with
210.20(A) through (D).
(A) Continuous and Noncontinuous Loads. Where a branch
circuit supplies continuous loads or any combination of continuous
and noncontinuous loads, the rating of the overcurrent
device shall not be less than the noncontinuous load plus
125 percent of the continuous load.
Exception: Where the assembly, including the overcurrent devices
protecting the branch circuit(s), is listed for operation at 100 percent of
its rating, the ampere rating of the overcurrent device shall be permitted
to be not less than the sum of the continuous load plus the noncontinuous
load.
210.19 Conductors — Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity
not less than the maximum load to be served. Conductors shall
be sized to carry not less than the larger of 210.19(A)(1)(a)
or (b).
(a) Where a branch circuit supplies continuous loads or
any combination of continuous and noncontinuous loads, the
minimum branch-circuit conductor size shall have an allowable
ampacity not less than the noncontinuous load plus
125 percent of the continuous load.
(b) The minimum branch-circuit conductor size shall
have an allowable ampacity not less than the maximum load to
be served after the application of any adjustment or correction
factors.
Exception: If the assembly, including the overcurrent devices protecting
the branch circuit(s), is listed for operation at 100 percent of its rating,
the allowable ampacity of the branch-circuit conductors shall be permitted
to be not less than the sum of the continuous load plus the noncontinuous
load.
You are stating an entirely different scenario than the op. He asked what is max continuous VA on 20A circuit. Your question is about a continuous 20A-rated load.Could someone provide the code reference stating you cannot have a continuous load more than 80% of a branch circuit's rating? This would imply you have the ability to reduce the draw on the appliance in use. How do you reduce the current draw on an appliance pre-assembled with plug n cord ready out of the box? I know we use 80% of circuit size as a good rule of thumb, but I haven't seen it as rule in the code book.
My understanding is: 20A x 120v = 2400VA is the load. Since it is a continuous load you would need a conductor rated at 20a x 1.25 or 25amps. "...minimum branch conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load."
210.21(A) states "Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load." Minimum OCPD is 20A × 125% = 24A, rounded up to next standard size 25A.My question is your terminals are rated at 75 degrees and you ran 12AWG THW (or any THHN for that matter), would that be code compliant? The OCPD wouldn't change, but the code is satisfied (even 240.4[D] ) to carry the calculated load now.
You are stating an entirely different scenario than the op. He asked what is max continuous VA on 20A circuit. Your question is about a continuous 20A-rated load.
210.21(A) states "Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load." Minimum OCPD is 20A × 125% = 24A, rounded up to next standard size 25A.
240.4(D)(5) you cannot use #12 copper with greater than a 20A breaker.
...
210.21(A) states "Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load." Minimum OCPD is 20A × 125% = 24A, rounded up to next standard size 25A.
...
Ummm... meant that to be 210.20(A)Got it. I overlooked 210.21 Would 10 AWG (romex/thhn/thw) with a 25 amp breaker satisfy this installation? Or as I stated previously, a 20A breaker rated at 100% with 12AWG THW?
Got it. I overlooked 210.21 Would 10 AWG (romex/thhn/thw) with a 25 amp breaker satisfy this installation? Or as I stated previously, a 20A breaker rated at 100% with 12AWG THW?
What is the load you are trying to supply?
Hmmm... a cord-and-plug-connected sound system that draws 20A continuous. Not possible unless all you play is pink noise at max volume for more than 3 hours at a time. :happyno:Hypothetically a cord and plug stereo system attached to a 20 duplex....(obviously a violation in the case of a 25 amp OCPD)
Hypothetically a cord and plug stereo system attached to a 20 duplex....(obviously a violation in the case of a 25 amp OCPD)
unless all you play is pink noise at max volume for more than 3 hours at a time.