210.19 Conductors — Minimum Ampacity and Size.
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity
not less than the maximum load to be served. Conductors shall
be sized to carry not less than the larger of 210.19(A)(1)(a)
or (b).
(a) Where a branch circuit supplies continuous loads or
any combination of continuous and noncontinuous loads, the
minimum branch-circuit conductor size shall have an allowable
ampacity not less than the noncontinuous load plus
125 percent of the continuous load.
(b) The minimum branch-circuit conductor size shall
have an allowable ampacity not less than the maximum load to
be served after the application of any adjustment or correction
factors.
Exception: If the assembly, including the overcurrent devices protecting
the branch circuit(s), is listed for operation at 100 percent of its rating,
the allowable ampacity of the branch-circuit conductors shall be permitted
to be not less than the sum of the continuous load plus the noncontinuous
load.