VA=watts

Status
Not open for further replies.

Timboe

Member
I have a plug in transformer that is 120v primary and 24v secondary. The rating stamped on it says 20va. I know this means apperant power but I was told that a good estimation is to think of VA as watts as in 20 watts. Does this mean that i should not put a load on this that is more than 20 watts?
 
Timboe said:
I have a plug in transformer that is 120v primary and 24v secondary. The rating stamped on it says 20va. I know this means apperant power but I was told that a good estimation is to think of VA as watts as in 20 watts. Does this mean that i should not put a load on this that is more than 20 watts?

It means,

Pa-max = 20VA = 24V*Iload-max

then,

Iload-max = 20VA/24V = 0.833A

You may overload the transformer if you treat apparent power as real power.
 