Mr. Serious
Senior Member
- Location
- Oklahoma, USA
- Occupation
- Electrical Contractor
I have a commercial customer I did some work for before. Last week they had the electric motor fail on their vacuum pump, and they searched online and found a new pump&motor combo unit that just bolts up to their tank. They have two choices, a 1HP unit that exactly replaces what they had, or a 1.5 HP unit.
1 HP 1-phase, 115/230 volts, 10.0/5.0 amps. Model number 7Z779
1.5HP 1-phase 115/230 volts, 15.2/8.2-7.6A. Model number 7Z782
Looks like the length, height, and inlet/outlet specifications match up well enough that either one could work.
Customer wants me to replace the pump, but also maybe add additional overload protection. I'm not sure what to do.
They have 3-phase power, 120/208Y. So, the original motor was running on 208 volts instead of the 230 it was rated for. The j-box at the motor location has two black #12 wires, but the circuit breaker is a 3-pole 30-amp breaker. I would want to at least change this to 20-amps. But is there anything else you would do? Should I plan on wiring the new motor for 115 instead of 230 because the voltage would match better? I probably would have to re-purpose one conductor as a neutral, all the way back to the panel. Or put a small auto-transformer?
And, is there anything else I should do to better protect the motor? The other thing I notice is that this room is very dusty. They have a vacuum pump and a compressor. The motors are inside a small closet where they are somewhat protected, but it's still dusty. The dust is probably what caused this to fail.
1 HP 1-phase, 115/230 volts, 10.0/5.0 amps. Model number 7Z779
1.5HP 1-phase 115/230 volts, 15.2/8.2-7.6A. Model number 7Z782
Looks like the length, height, and inlet/outlet specifications match up well enough that either one could work.
Customer wants me to replace the pump, but also maybe add additional overload protection. I'm not sure what to do.
They have 3-phase power, 120/208Y. So, the original motor was running on 208 volts instead of the 230 it was rated for. The j-box at the motor location has two black #12 wires, but the circuit breaker is a 3-pole 30-amp breaker. I would want to at least change this to 20-amps. But is there anything else you would do? Should I plan on wiring the new motor for 115 instead of 230 because the voltage would match better? I probably would have to re-purpose one conductor as a neutral, all the way back to the panel. Or put a small auto-transformer?
And, is there anything else I should do to better protect the motor? The other thing I notice is that this room is very dusty. They have a vacuum pump and a compressor. The motors are inside a small closet where they are somewhat protected, but it's still dusty. The dust is probably what caused this to fail.