I have asked the member who posted this voltage drop example below to confirm it was created using ETAP, validated and verified (V&V) against IEEE and several other standards.
Me and Smart $ had comparative results using formulas from Note #2 of NEC Table 8 & 9, but my results only match the V&V example above using 420 Amps rather than the 400 provided.
I suspect this ETAP example has done something important to the amperage, which me and Smart are both missing. Could this I = (Watts / Phases / L-to-N voltage) have something to do with it.
kingpd said:Assuming 480V, 400A, 750ft, pf= 0.85, above ground installation of magnetic conduit, and limiting VD = 2%
(1 set) 1/C 600 KCMIL = 5.3% VD
(2 set) 1/C 600 KCMIL = 2.6% VD
(3 set) 1/C 500 KCMIL = 1.8% VD
if installation is underground duct, using PVC, then;
(2 set) 1/C 500 KCMIL = 2.4% VD
(3 set) 1/C 350 KCMIL = 2.0% VD
Me and Smart $ had comparative results using formulas from Note #2 of NEC Table 8 & 9, but my results only match the V&V example above using 420 Amps rather than the 400 provided.
I suspect this ETAP example has done something important to the amperage, which me and Smart are both missing. Could this I = (Watts / Phases / L-to-N voltage) have something to do with it.