Hello all my stupid question is to validate a Ongoing debate 120/208 v
we have 6 20 amp 120v circuits drawing 16 amps each 1920w x6 =96 amps correct !
we also have a environmental control unit 3 phase 208 5500w divided by 360 =15.27 amps +96 amps total load would be 111.27 = 125 amp main ,am i thinking about this right or should I be taking the total watts of both 1920 and 5500 adding together total watts 1920+5500 divided by 360 for total ,Load on the 120/208 service My thought is you have to separate the 3 phase loads form the single phase loads,
we have 6 20 amp 120v circuits drawing 16 amps each 1920w x6 =96 amps correct !
we also have a environmental control unit 3 phase 208 5500w divided by 360 =15.27 amps +96 amps total load would be 111.27 = 125 amp main ,am i thinking about this right or should I be taking the total watts of both 1920 and 5500 adding together total watts 1920+5500 divided by 360 for total ,Load on the 120/208 service My thought is you have to separate the 3 phase loads form the single phase loads,