Variable speed drive grounding

Status
Not open for further replies.

PowerdT

Senior Member
Location
San Diego
Occupation
Electrical Engineer
Do we need GEC or EGC for VSD system?

Customer is asking for ground rod? The input that feeds the VSD is 3 Hot and EGC. I am not sure why we need ground rod.

Any help please.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Do we need GEC or EGC for VSD system?

Customer is asking for ground rod? The input that feeds the VSD is 3 Hot and EGC. I am not sure why we need ground rod.

Any help please.
Regardless of whether you have a GEC or not, you will need an EGC.

I doubt it matters much one way or the other if you add a ground rod for a VFD. But not a code requirement. Some people like to pay extra for stuff that serve no real purpose.
 

PowerdT

Senior Member
Location
San Diego
Occupation
Electrical Engineer
Regardless of whether you have a GEC or not, you will need an EGC.

I doubt it matters much one way or the other if you add a ground rod for a VFD. But not a code requirement. Some people like to pay extra for stuff that serve no real purpose.
I thought it helps on the noice level?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
We've installed a thousand drives and never once connected it an electrode. Requiring a connection to one sounds like junk science and a waste of money.
 

4-20mA

an analog man in a digital world
Location
Charleston SC
Occupation
Instrumentation & Electrical
We've installed a thousand drives and never once connected it an electrode. Requiring a connection to one sounds like junk science and a waste of money.
Same... But maybe only like tens of tens for me.
 