Do we need GEC or EGC for VSD system?

Customer is asking for ground rod? The input that feeds the VSD is 3 Hot and EGC. I am not sure why we need ground rod.

Any help please.
 
Do we need GEC or EGC for VSD system?

Customer is asking for ground rod? The input that feeds the VSD is 3 Hot and EGC. I am not sure why we need ground rod.

Any help please.
Regardless of whether you have a GEC or not, you will need an EGC.

I doubt it matters much one way or the other if you add a ground rod for a VFD. But not a code requirement. Some people like to pay extra for stuff that serve no real purpose.
 
Regardless of whether you have a GEC or not, you will need an EGC.

I doubt it matters much one way or the other if you add a ground rod for a VFD. But not a code requirement. Some people like to pay extra for stuff that serve no real purpose.
I thought it helps on the noice level?
 
We've installed a thousand drives and never once connected it an electrode. Requiring a connection to one sounds like junk science and a waste of money.
 
We've installed a thousand drives and never once connected it an electrode. Requiring a connection to one sounds like junk science and a waste of money.
Same... But maybe only like tens of tens for me.
 