Variable Wattage Lamps

Status
Not open for further replies.

solaeros

Member
Location
Beautiful IDAHO


Ok I'm told you can't run a lower rated lamp from what the luminaire itself is rated for ie: 250 watt MH Lamp in a 400 Watt MH Luminaire. I don't understand this, to me it's like saying you'll burn up a 100 amp service if run off a 100kva transformer. Shouldn't the lamp create the load and not the ballast? Would it be a capacitor issue? Could it be a wives tale?
 

mdshunk

Senior Member
Location
Right here.
The capacitor and the starting device are sized for the particular wattage of the lamp. That would be like taking the cap and potential relay for a 3 horse motor and trying to use it for a 1 horse motor. Ain't gonna work, or at least won't work for long.
 

iwire

Moderator
Staff member
Location
Massachusetts
Along with Marc's comments I will add that is also important that the ballast match the lamp.

A ballast does not supply a constant voltage to the lamp, the ballast maintains a certain current in the circuit. The lamps are designed to run at certain current.

If you where to wire a typical HID lamp directly to the line the current it draws would keep escalating as it warmed until it tripped the circuit.
 