I always see VAV's on blueprints with a toggle disconnect switch. Is that code to have means of disconnect at the VAV? THanks.
It is still required but there is some dispensation to use the branch circuit OCPD as the motor disconnect for small motors.The motors are small enough that I don't believe any disconnect is required for each VAV, although one might be required for the transformer.
So how does that fit in with 430.109 B, which says that for stationary motors of 1/8 HP or less, the branch circuit OCP is permitted to serve as the disconnecting means?Every motor requires a disconnect, including bath exhaust fans, electric clocks…disconnect typically must be within sight of motor, please review 430.102
You can often use the controller disconnect as the motor disconnect, and sometimes you can use the branch circuit OCPD as the motor disconnect. But, you still have to have a motor disconnect.So how does that fit in with 430.109 B, which says that for stationary motors of 1/8 HP or less, the branch circuit OCP is permitted to serve as the disconnecting means?
I'm never sure if 430.109 B applies to the disconnect at the motor, or to the one at the controller, or to both required disconnects.
And 422.31 (A) says that the branch circuit OCP may be permitted to serve as the disconnecting means for an appliance.
I take those two paragraphs to mean we can forgo the disconnect at each VAV, and just use the branch circuit OCP for a disconnect to multiple VAV's.