VD & 20A Ckts

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Have a 208v motor feed from a 1P-20a circuit. The motor is about500’ away. I’m coming up with #8’s in a single conduit…if I combine a 3 circuithomerun I’m coming up with #6’s. This is to keep the VD under 3%. Does thismake sense and if so I can’t use a 20a breaker. Correct? Thanks.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Without knowing more details, an alternative might be to run a feeder to a sub-panel near the loads, if I'm understanding your "3 circuit home run" correctly.
 