How would you do a VD calc for wiring running to (15) lights in a row. Thinking about what would be entered for "current at the end of the run"?
220.18(B) wont allow WattsI'm a littler lost. So if each fixture is 50 watts I'd do what?
I'm a littler lost. So if each fixture is 50 watts I'd do what?
If nameplate is missing Amps the lights are illegal, and fire marshals report it as a fire hazard.The simplest calculation (watts / volts = amps)
Convert it to amps. Amps = Watts/ Volts.I'm a littler lost. So if each fixture is 50 watts I'd do what?
I think I would start at the source end.Convert it to amps. Amps = Watts/ Volts.
I usually like to start at the last fixture and work my way back to the source;
Amps * distance * "VoltDrop per amp-foot" for first light and add each segment using the current and length for each segment.
Here is an example: 120 Watt fixtures, 120 Volts each, so 1 amp per light. Assume they are 100' apart with #12 wire. Assume there are 10 lights.
My square d calculator gives 0.37 volts drop per amp per 100' for #12, or .0037 per amp-foot.
1 amp * 100' * .0037 + 2 amps * .0037 * 100' + 3 amps * .0037 * 100'.....
After thinking about it, you will have .37 * (1+2+3+4....10) or .37* 55 = 20.4 volts drop at the last light if I didn't make a mistake.
We would problaby want larger wire for that run.
The answer is the same, so do whichever it's easier to wrap your mind around.I think I would start at the source end.
This works as long as the run is all one conductor size. If you have more than one conductor size in the run, you need to do each segment separately.Amps * distance * "VoltDrop per amp-foot" for first light and add each segment using the current and length for each segment.