Hello everyone. I’m looking at rewiring an existing residential dock. Original branch circuit is supplied by a two-pole 40amp with 6-3 Romex from the panel that runs 75-85ft through the attic to a junction box on the side of the house. From there it is 165ft to the dock. So total length from the panel to the dock is 240-250ft. The load at the dock is a 12.5amps lift plus a few led lights.
I plan on running 6awg THWN in 1in PVC to the dock. By my calculation the VD wouldn’t be more than 5volts.
I used 2 x 12.9 x 20 x 250/26,240= 4.92 for my calculation.
I’m just wanting to make sure I’m correct, and also wanted to know what your thoughts are on changing the breaker out to a two-pole 40amp GFCI? Thanks