I was sent an email from a fellow Tulsa electrician asking me to do a Voltage drop on a feeder. I was like sure what you got.
This is the info he gave me.
System Voltage 208/120 three pahse four wire
Three phase four wire feeder from MDP to New 400 amp main lug panel for kitchen equipment 421 feet.
Circuit amps 205.85 Max unbalanced neutral load 115 amps
Breaker in MDP 250 amp
Feeder is ran in a ceiling of conditioned space (open bar joist) 18" down from ceiling. No ambient correction
He and I both come up with a single 350 mcm copper
The engineer said two set of 350 MCM. He told me he ask the engineer to check and came back with the same number.
From engineer: (2) set 350 mcm cu with a VD of 2.8%
I inputted a 2% just in case and still did not come up with 2-350's I even ran the 5% over all based on largest load.
I did tell him an engineer designed it and should follow his recommendation. This is more for me to learn.
Any advise as to where I may have went wrong?
This is the info he gave me.
System Voltage 208/120 three pahse four wire
Three phase four wire feeder from MDP to New 400 amp main lug panel for kitchen equipment 421 feet.
Circuit amps 205.85 Max unbalanced neutral load 115 amps
Breaker in MDP 250 amp
Feeder is ran in a ceiling of conditioned space (open bar joist) 18" down from ceiling. No ambient correction
He and I both come up with a single 350 mcm copper
The engineer said two set of 350 MCM. He told me he ask the engineer to check and came back with the same number.
From engineer: (2) set 350 mcm cu with a VD of 2.8%
I inputted a 2% just in case and still did not come up with 2-350's I even ran the 5% over all based on largest load.
I did tell him an engineer designed it and should follow his recommendation. This is more for me to learn.
Any advise as to where I may have went wrong?
VD | VOLTS | 3-p | Exact K | D | I | CM | AWG | VD % |
3.55 | 120 | 2 | 12.845 | 421 | 115 | 350000 | 350 | 2.96% |
5.51 | 208 | 1.732 | 12.845 | 421 | 205.85 | 350000 | 350 | 2.65% |
CM=( pahse x Ka x distnce x I)/VP permited | ||||||||
cm | CU | 3% | ||||||
3 phase | app K | Feet | Amps | VD p | ||||
(N) | 346,974 | 350 | 350 | 2 | 12.9 | 421 | 115 | 3.6 |
(P) | 310,303 | 350 | 350 | 1.732 | 12.9 | 421 | 205.85 | 6.24 |
Phase Conductors | |||||
AMP | AWG | CM | RATIO | ||
OCD | 250 | ||||
CM | Selected | 250 | 250,000 | ||
CM | Requireds | 350 | 350,000 | ||
EGC Rtaio | 1.40000 | ||||
EGC | OLD | 4 | 41,740 | ||
NEW | 2 | 66360 | 58,436 |
(t) | ||||
cycle | HZ | seconds | ||
0.5 | 60 | 0.008333333 | ||
CM | / 42.5 | I² | ||
#2 | 66360 | 1570.651 | 2,466,944 | |
I² | (t) | (CWR) | ||
2,466,944 | 5 | 12,334,721 | ||
I²T @1/2 cycle | 38,473 | AMPS |
Jam Ratio | ||||
EMT | (D) | AWG | (d) | Ratio |
2 1/2 | 2.731 | 350 | 0.817 | 3.34 |