I was sent an email from a fellow Tulsa electrician asking me to do a Voltage drop on a feeder. I was like sure what you got.
This is the info he gave me.
System Voltage 208/120 three pahse four wire
Three phase four wire feeder from MDP to New 400 amp main lug panel for kitchen equipment 421 feet.
Circuit amps 205.85 Max unbalanced neutral load 115 amps
Breaker in MDP 250 amp
Feeder is ran in a ceiling of conditioned space (open bar joist) 18" down from ceiling. No ambient correction

He and I both come up with a single 350 mcm copper
The engineer said two set of 350 MCM. He told me he ask the engineer to check and came back with the same number.
From engineer: (2) set 350 mcm cu with a VD of 2.8%

I inputted a 2% just in case and still did not come up with 2-350's I even ran the 5% over all based on largest load.

I did tell him an engineer designed it and should follow his recommendation. This is more for me to learn.

Any advise as to where I may have went wrong?
VDVOLTS3-pExact KDICMAWGVD %
3.55120212.8454211153500003502.96%
5.512081.73212.845421205.853500003502.65%

CM=( pahse x Ka x distnce x I)/VP permited
cmCU
3%​
3 phaseapp KFeetAmpsVD p
(N)
346,974​
350350
2​
12.9​
421​
115​
3.6​
(P)
310,303​
350350
1.732​
12.9​
421​
205.85​
6.24​
Phase Conductors
AMPAWGCMRATIO
OCD250
CMSelected250250,000
CMRequireds350350,000
EGC Rtaio1.40000
EGCOLD441,740
NEW26636058,436

(t)
cycleHZseconds
0.5600.008333333
CM/ 42.5
#2663601570.6512,466,944
(t)(CWR)
2,466,944512,334,721
I²T @1/2 cycle38,473AMPS

Jam Ratio
EMT(D)AWG(d)Ratio
2 1/2​
2.7313500.8173.34
 
I see it's based @ 60c and 90%pf
I should have used 90% since it's comm kitchen loads.
I will change my number from 30c to 90c and use 90%pf
Thanks
 
I see it's based @ 60c and 90%pf
I should have used 90% since it's comm kitchen loads.
I will change my number from 30c to 90c and use 90%pf
Thanks
Tbh I never even paid much mind to the temp and PF numbers, I seen them but that was about it.

I typically don’t use apps but just the over simplified calculation on paper.
 
I see it's based @ 60c and 90%pf
I should have used 90% since it's comm kitchen loads.
I will change my number from 30c to 90c and use 90%pf
Thanks

421 feet is a long way for 120 volt loads. Might consider a transformer for future expansion near the kitchen.

205A Neutral VD = 2.67% with 4/0cu x 2 parallel, using home made AC formula spreadsheet.

Verified & validated engineering systems may be more accurate, since me poor man's NEC Table 9 impedances are only good at pf=0.85
 
Oops! I screwed up too Dsg319! I was thinking op was going underground, but he is going overhead, so it will probably be in EMT.
 