I am upsizing my wire to 350kcmil AL for voltage drop. Therefore I have to proportionally upsize the EGC.
It has to be at least 12.5% of the ungrounded conductor correct?
So 350 kcmil = .364 found in conductor properties page 705
my EGC must be at least .0455 = #3 AL
Can someone tell me if this is correct?