So when doing voltage drop calc and you have 3P 4W feeder from 277/480 panel to another 277/480 panel is the feeder 277 or 480? And why? Thanks
Is there a common example where the transient state loading will end up controlling, and it won't be sufficient to just look at the steady state?If you really want to get into the weeds on VD calculations, you need to consider both transient (eg. motor starting) and steady state loading, but common practice is to calculate voltage drop in the steady state.
Is there a common example where the transient state loading will end up controlling, and it won't be sufficient to just look at the steady state?
Cheers, Wayne
So when doing voltage drop calc and you have 3P 4W feeder from 277/480 panel to another 277/480 panel is the feeder 277 or 480? And why? Thanks
No reason to not do it this way, unless there is a physical constraint such as installed cable or conduit that isn't being replaced.For unbalanced 3-phase loads, consider the worst case scenario total line current among the entire circuit, ans use that as the basis of the calculation.