Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
Do you experience less voltage drop with a cable like SER or MC then you would with a rigid pipe with wires?
Fortunately, I have little experience with either. Make that none.I thought maybe this was going to be a medical question.
See the "Effective Z" columns in Chapter 9, Table 9, for an example of the effect. I assume a cable with a non-metallic sheath (e.g. SER) would be akin to PVC conduit, while aluminum MC would be akin to aluminum conduit, and steel MC would be akin to steel conduit.Do you experience less voltage drop with a cable like SER or MC then you would with a rigid pipe with wires?
theoretically, it comes down to a question of how the cable and conduit/MC sheathing geometry affects the reactance. I would expect capacitive reactance to increase as the distance from sheathing to conductors decreases like a tube capacitor. to what degree, i defer to those much smarter than myself.Do you experience less voltage drop with a cable like SER or MC then you would with a rigid pipe with wires?
I'm coming up with different sizes on diff calculators. Can someone check.
480v
800A load at end
600'- run in mc cable
CU = 4 sets #250
AL = 4 sets #400