Do you experience less voltage drop with a cable like SER or MC then you would with a rigid pipe with wires?
See the "Effective Z" columns in Chapter 9, Table 9, for an example of the effect. I assume a cable with a non-metallic sheath (e.g. SER) would be akin to PVC conduit, while aluminum MC would be akin to aluminum conduit, and steel MC would be akin to steel conduit.

Cheers, Wayne
 
Do you experience less voltage drop with a cable like SER or MC then you would with a rigid pipe with wires?
theoretically, it comes down to a question of how the cable and conduit/MC sheathing geometry affects the reactance. I would expect capacitive reactance to increase as the distance from sheathing to conductors decreases like a tube capacitor. to what degree, i defer to those much smarter than myself.

 
I'm coming up with different sizes on diff calculators. Can someone check.

480v
800A load at end
600'- run in mc cable

CU = 4 sets #250
AL = 4 sets #400
 
I'm coming up with different sizes on diff calculators. Can someone check.

480v
800A load at end
600'- run in mc cable

CU = 4 sets #250
AL = 4 sets #400

Unsure what you are looking for but.....

Using Mike's free calculator those 2 runs are comparable with both giving you about 10 volts drop
 