Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
So I have some 20A 120v receptacles that are about 150-200' away from panel.
About 20 of them on more than a few circuits,
I don't think 12/2 mc cable( for each circuit) would work due to voltage drop.
A few questions.
1. I think it would make more sense to run pipe and wire to the are the drop down with MC from there. I know I need to consider derating for # of ccc's.
2. If one was to run MC from the location to a box near the panel( about 150'-200' away) what size cable? I ran a calc and came up with #8's. I don;t think that's right.
THanks.
About 20 of them on more than a few circuits,
I don't think 12/2 mc cable( for each circuit) would work due to voltage drop.
A few questions.
1. I think it would make more sense to run pipe and wire to the are the drop down with MC from there. I know I need to consider derating for # of ccc's.
2. If one was to run MC from the location to a box near the panel( about 150'-200' away) what size cable? I ran a calc and came up with #8's. I don;t think that's right.
THanks.