VE Genset Size

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
Engineer looking to go to 350KW genset from this 750. Would have to reduce switchboard and loads obviously, correct? Thanks
 

Attachments

  • Capture.jpg
    Capture.jpg
    19.3 KB · Views: 0

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Engineer looking to go to 350KW genset from this 750. Would have to reduce switchboard and loads obviously, correct? Thanks
Not necessarily. The generator will have a breaker. The loads need to be less that the 350KW, but what you sent doesn't really represent what the loads are. Many times the biggest issue is the HVAC all wanting to start up at the same time. It isn't uncommon to put delay timing scheme on HVAC to prevent this allowing for a smaller generator.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Engineer looking to go to 350KW genset from this 750. Would have to reduce switchboard and loads obviously, correct? Thanks

My guess is that they're eliminating the optional standby loads therefore reducing the generator size. The other loads cannot be eliminated.
 