VE Options

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
We have a job in which there a good amount of MI cable but I was thinking of offering a VE option to use conduit with RHH 2 hour rated? Any reason why that could NOT be used? For some reason I'm thinking fire pump must be MI.
 
We have a job in which there a good amount of MI cable but I was thinking of offering a VE option to use conduit with RHH 2 hour rated? Any reason why that could NOT be used? For some reason I'm thinking fire pump must be MI.
As long as you get the 2-hour rating, it doesn't matter what you use. Make sure there aren't any restrictions in the job specs OR buried deep in a drawing note. Being careless can get expensive.
 