So MDP to the (7) sub panel is an average of about 80' each.
Wire is run in RGS conduit.
I'm thinking instead of running (7) separate 3/4" conduits it may be more efficient to combine. Obvious need to derate.
If I was to combine two runs( that would be 2#6's and I'm assuming a neutral and ground) I would be at the 4-7 conductor derating and 80%. Using the 90 degree column I still get 60A? Is that correct for the 60A circuits. Obviously have to upsize conduit.
Last pic is typical sub panel schedule.



Wire is run in RGS conduit.
I'm thinking instead of running (7) separate 3/4" conduits it may be more efficient to combine. Obvious need to derate.
If I was to combine two runs( that would be 2#6's and I'm assuming a neutral and ground) I would be at the 4-7 conductor derating and 80%. Using the 90 degree column I still get 60A? Is that correct for the 60A circuits. Obviously have to upsize conduit.
Last pic is typical sub panel schedule.