This is in a rural setting where the poco commonly mounts a meter that has an integrated manual transfer switch, so you manually select between utility power and generator.
HO has a 10 kW vehicle mounted (military surplus) generator. The "vehicle" has receptacles mounted on it in the form of a construction site spider box. It appears to have "feed through" capability with a 50 amp 4-wire twist-lock feeding into it from the generator, then a 50-amp female plug (twist lock) on the opposite side.
the spider box has CB's to protect the other receptacle mounted on it.
He wants to use a 4-wire pigtail out of this spider box to feed a 50-amp inlet at the manual transfer switch in the meter box (neutral is not switched).
From the meter/manual transfer switch location service conductors (3-wire) feed to various locations on the property, including the house which has a 200-amp service panel.
The meter location is not considered the service disconnect by the poco and the electrical AHJ, it's considered a "site isolating switch". Each structure that is fed by this meter is set up as a service with neutral ground bond.
Basicly we're trying to decide whether the neutral and ground at the generator need to be bonded or not, given the situation?
HO has a 10 kW vehicle mounted (military surplus) generator. The "vehicle" has receptacles mounted on it in the form of a construction site spider box. It appears to have "feed through" capability with a 50 amp 4-wire twist-lock feeding into it from the generator, then a 50-amp female plug (twist lock) on the opposite side.
the spider box has CB's to protect the other receptacle mounted on it.
He wants to use a 4-wire pigtail out of this spider box to feed a 50-amp inlet at the manual transfer switch in the meter box (neutral is not switched).
From the meter/manual transfer switch location service conductors (3-wire) feed to various locations on the property, including the house which has a 200-amp service panel.
The meter location is not considered the service disconnect by the poco and the electrical AHJ, it's considered a "site isolating switch". Each structure that is fed by this meter is set up as a service with neutral ground bond.
Basicly we're trying to decide whether the neutral and ground at the generator need to be bonded or not, given the situation?