I know that such generator is not required to be grounded (earth) if it is only supplying receptacles mounted on the vehicle, trailer, or the generator itself.
If the correct conditions are met.
Such as the generator frame is bonded to the vehicle and or trailer frame, and the normally non current carrying metal parts of equipment and the EGC terminals of the receptacles are connected to the generator frame.
Also the generator manufacturer is required to bond neutral conductor to the generator frame under these following conditions.
1.) The generator is a component of a separately derived system.
2.)A grounding type receptacles is mounted on the generator or is supplied by the generator.
3.) A receptacle on the generator is supplied by the generator with GFCI protection.
With having said all that, I understand when just using cord and plug equipment From the generator receptacles grounding is not required.
hypothetical scenario.... 20kw BONDED gen, trailer mounted genset, feeding a 100amp distribution panel from (not a receptacle) but from load terminals on the genset with OCPD.
Temporarily supplying power to part of a station, no ATS or nothing like that just temp power.
Should the genset than be required to be grounded since it’s supplying Power from the terminals and not a recep?
If the correct conditions are met.
Such as the generator frame is bonded to the vehicle and or trailer frame, and the normally non current carrying metal parts of equipment and the EGC terminals of the receptacles are connected to the generator frame.
Also the generator manufacturer is required to bond neutral conductor to the generator frame under these following conditions.
1.) The generator is a component of a separately derived system.
2.)A grounding type receptacles is mounted on the generator or is supplied by the generator.
3.) A receptacle on the generator is supplied by the generator with GFCI protection.
With having said all that, I understand when just using cord and plug equipment From the generator receptacles grounding is not required.
hypothetical scenario.... 20kw BONDED gen, trailer mounted genset, feeding a 100amp distribution panel from (not a receptacle) but from load terminals on the genset with OCPD.
Temporarily supplying power to part of a station, no ATS or nothing like that just temp power.
Should the genset than be required to be grounded since it’s supplying Power from the terminals and not a recep?