- Chapel Hill, NC
- Retired Electrical Contractor
Am I correct in saying that a vending machine need not be fed with a gfci circuit if the vending machine has a gfci integral with the cord cap? Assume that the vending machines are not located in an area requiring a gfci, ie, outdoors. Also, this means the receptacle cannot be behind the machine
422.5(A) General.
Appliances identified in 422.5(A)(1) through (A)(7) rated 150 volts or less to ground and 60 amperes or less, single- or 3-phase, shall be provided with Class A GFCI protection for personnel. Multiple Class A GFCI protective devices shall be permitted but shall not be required.
(B) Type and Location.
- (1)Automotive vacuum machines
- (2)Drinking water coolers and bottle fill stations
- (3)Cord-and-plug-connected high-pressure spray washing machines
- (4)Tire inflation machines
- (5)Vending machines
- (6)Sump pumps
- (7)Dishwashers
The GFCI shall be readily accessible, listed, and located in one or more of the following locations:
- (1)Within the branch-circuit overcurrent device
- (2)A device or outlet within the supply circuit
- (3)An integral part of the attachment plug
- (4)Within the supply cord not more than 300 mm (12 in.) from the attachment plug
- (5)Factory installed within the appliance