Is there a standard that governs wire sizing for vendor equipment? I see equipment regularly where the "internal" wiring does not appear to be protected. E.g., control wiring (14, 16, 18 AWG) that is fed from the secondary side of the main breaker/fuse (80, 100, 125 A) feeding the major equipment loads. I understand NEC doesn't govern in this case, but I'm not sure if there is some other standard that would govern and provide guidance on what is safe.
I know switchgear manufacturers will routinely use a 30 A fuse to "protect" the breaker trip circuit that uses 14 AWG panel wiring. Their reasoning is usually that it is more important to ensure power to trip circuit if at all possible. Though I have yet to find a manufacturer that will explain why they don't use larger conductors in the trip circuit as well. I haven't looked at the auto-ignition curves, but perhaps there is an argument to be made there. I have generally accepted this configuration because it seems to be standard across manufacturers, but what about cases with much larger protective devices supplying the same size control wiring in other applications?
I know switchgear manufacturers will routinely use a 30 A fuse to "protect" the breaker trip circuit that uses 14 AWG panel wiring. Their reasoning is usually that it is more important to ensure power to trip circuit if at all possible. Though I have yet to find a manufacturer that will explain why they don't use larger conductors in the trip circuit as well. I haven't looked at the auto-ignition curves, but perhaps there is an argument to be made there. I have generally accepted this configuration because it seems to be standard across manufacturers, but what about cases with much larger protective devices supplying the same size control wiring in other applications?