Vented Panels on 4160VAC Switchgear

Status
Not open for further replies.

buffalonymann

Senior Member
Location
NC
My facility installed new 4160VAC switchgear about 16 months ago; the enclosure rear access panels are vented. I can't remember ever seeing vented access panels on medium voltage gear. Anybody care to comment?
 

ron

Senior Member
Not unusual.

Unless the equipment is listed as arc resistant and tested per IEEE C37.20.7[FONT=Arial, Arial, sans-serif] (which yours is not with vented panels in the rear), the doors should always be considered to be shrapnel during a fault.[/FONT]
 

Tony S

Senior Member
Once you see the aftermath of a MV flashover you’ll realise why they vent to the back. We had a 50 year old 11kV OCB flashover. Had anyone been at the front they would have been dead. The switchroom looked like a bomb had gone off, the shrapnel had to be chiselled out of the brickwork.

Even LV gear can be a death trap. A fire on one of our plants forced me open a dependant manual switch on load. I’d been taught the “left hand rule” never stand directly in front of a switch. The cast iron front blew out, I was just slightly singed.
 