I am a lot more competent when it comes to the selection of proper equipment and protection techniques. Although definitely no expert, I have been wrestling with that for more than five years now. I feel like if I know what the area classification is, then I at least know what I don't know when it comes to protection techniques, and know when to go back and study NFPA 70 for direction.
The problem I see more often now is that the process equipment that is being designed as CID2, is the actual source of the hazardous area. Take the case study situation of an automobile manufacturing plant that is introducing flammable refrigerants for the first time. These entire facility may be the size of a small midwestern town, and now this chunk of the assembly line is now charging flammable material.
To me, the most important part of the entire puzzle is the ventilation system. Without "adequate ventilation", then CID2 does not exist. I understand the different approaches to quantifying adequate ventilation as the general "4 exchanges of air" or the more analytical approaches in API RPI 500. But the actual mechanics of the ventilation system is where I struggle.
Does the entire facilities ventilation system come in to play, or just the local ventilation around the process area?
The larger plants ventilation system is what is providing the 4 exchanges of air per hour, and is what is being used to determine "adequate ventilation". If i am using this ventilation system to get adequate ventilation, and from it deem the area Class I Div 2, what are the requirements for the ventilation system motor? CID1 protection methods, CID2, or non classified?
Once I get the ventilation requirements figured out, and can confidently say I have adequate ventilation, then I would apply the Point Release method form API RP 500 to define the extents of the classified area.