We're developing a plant standard for racking medium voltage breakers. Our position is to completely de-energize the gear we will be working in, but we've hit a hurdle when it comes to testing for voltage.
As I read NFPA 70E it seems like the only acceptable way to check voltage is to put on a 40 cal. suite, and class 2 gloves and go into the energized 4160 volt cubicle with the appropriate tester on a hot-stick; check the bus to confirm tester operation; then de-energize and re-test the bus.
PPE or not, I would really like to avoid going into any energized MV cubicles for any reason.
Would it be considered an effective test to put on appropriate PPE, check the low-voltage side of the potential transformers (120 volts) prior to de-energizing, then de-energize and re-check the PTs?
OR would it be acceptable to use the switchgear metering to determine the presence of voltage? There are multiple meters that could check the same bus, giving us a level of redundancy.
Are there any standards that lay this out in black and white? I'm looking for answers because the irony here is that it seems like the voltage checks designed to ensure safety are in fact on of the most dangerous parts of this operation.
-John
As I read NFPA 70E it seems like the only acceptable way to check voltage is to put on a 40 cal. suite, and class 2 gloves and go into the energized 4160 volt cubicle with the appropriate tester on a hot-stick; check the bus to confirm tester operation; then de-energize and re-test the bus.
PPE or not, I would really like to avoid going into any energized MV cubicles for any reason.
Would it be considered an effective test to put on appropriate PPE, check the low-voltage side of the potential transformers (120 volts) prior to de-energizing, then de-energize and re-check the PTs?
OR would it be acceptable to use the switchgear metering to determine the presence of voltage? There are multiple meters that could check the same bus, giving us a level of redundancy.
Are there any standards that lay this out in black and white? I'm looking for answers because the irony here is that it seems like the voltage checks designed to ensure safety are in fact on of the most dangerous parts of this operation.
-John