Ok. I just want to verify I am correct on this.
Someone installed a single phase 240/480 to 120/240 50KVA transformer on rooftop. The feed is a 2 wire + 1 ground (2) #2 and (1) #6 gnd
This is what they put in. I think it?s incorrect
Source (3 phase 200A switch gear) to a 200A Meter then to a 100A Service disconnect 600V switch to a single phase 50KVA transformer with (2) #2 & (1) #6 gnd wire ( approximately 50 ft). The secondary conductor is (3) #3/0 &(1) 4 gnd to a 200A main breaker panel. The total load is 36.88KVA which is about 154A.
I think they should be using a 150A disconnect and (2) #1/0 & (1) #6 gnd conductors on the primary side and a 150A meter. The primary side OCPD based on 450.3(B)
Transformer rated at 50KVA/480V = 104A
With 125% it?s at 130A. So the next size up based on 240.6(A) is 150A.
Since this is rooftop, I check make sure the ambient temperature adjustment is ok.
Ambient temp = 34C - so factor is 0.96 based on 310.15(B)(2)(a). Conductor #1/0 is rated at 170A @ 90C
170X0.96 = 163.2 A
@75C #1/0 is rated at 150A. So the ampacity is 150A
Am I correct on the OCPD and ambient temperature adjustment ?
Someone installed a single phase 240/480 to 120/240 50KVA transformer on rooftop. The feed is a 2 wire + 1 ground (2) #2 and (1) #6 gnd
This is what they put in. I think it?s incorrect
Source (3 phase 200A switch gear) to a 200A Meter then to a 100A Service disconnect 600V switch to a single phase 50KVA transformer with (2) #2 & (1) #6 gnd wire ( approximately 50 ft). The secondary conductor is (3) #3/0 &(1) 4 gnd to a 200A main breaker panel. The total load is 36.88KVA which is about 154A.
I think they should be using a 150A disconnect and (2) #1/0 & (1) #6 gnd conductors on the primary side and a 150A meter. The primary side OCPD based on 450.3(B)
Transformer rated at 50KVA/480V = 104A
With 125% it?s at 130A. So the next size up based on 240.6(A) is 150A.
Since this is rooftop, I check make sure the ambient temperature adjustment is ok.
Ambient temp = 34C - so factor is 0.96 based on 310.15(B)(2)(a). Conductor #1/0 is rated at 170A @ 90C
170X0.96 = 163.2 A
@75C #1/0 is rated at 150A. So the ampacity is 150A
Am I correct on the OCPD and ambient temperature adjustment ?