Verifying Ground Resistance testing of grounding rods

Status
Not open for further replies.

TVH

Senior Member
Is there a safe and simple way to verify ground resistance readings of driven electrodes without having to conduct extensive ground resistance testing? We have many large portable generators on our construction sites that are moved frequentely and testing of the required driven electrode can become unmanageable.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Is there a safe and simple way to verify ground resistance readings of driven electrodes without having to conduct extensive ground resistance testing? We have many large portable generators on our construction sites that are moved frequentely and testing of the required driven electrode can become unmanageable.

Forgo the testing and ake an extra 5 minutes to drive two rods, maybe?

What I don't like about rod electrode testing is it only gives you a value for that particular point in time. The readings will change with the weather and I mean that literally. What passes today may fail tomorrow or vice versa.
 

zog

Senior Member
Location
Charlotte, NC
Is there a safe and simple way to verify ground resistance readings of driven electrodes without having to conduct extensive ground resistance testing? We have many large portable generators on our construction sites that are moved frequentely and testing of the required driven electrode can become unmanageable.

A 3 point test only takes about 30 minutes, how frequently are you moving them?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Just a few questions. Do they really need to be grounded? Have you read 250.34?

And even if they do infact have to be grounded, why the concern over the earth resistance?

Roger
 