I’ve got a two inch RMC conduit going vertical from a disconnect switch.
Does it need to be supported at 3’? Or can it be supported at 20’ from the connection at the top of the enclosure?
Thanks


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
344.30(B) states "securely fastened at top and bottom"and (A) states "securely fasten within 3 ft of ...box"
 