Is it permissible to run EMT vertically on the inside channel of a metal stud?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
I'm guessing that he worried about a screw penetrating the EMT. There is no 1.25" setback rule for EMT so it could be run close to the face of the metal stud without protection.
If someone does drive a screw in such a situation, would the person be able to know that there is EMT in that stud, while driving the screw?
Probably best to follow the 1.25" setback rule anyway, to avoid the risk of this happening.
IMO the severe physical damage protection requirement is for after the wall is finished not before.
So the building owner installs a fixture on the wall, years after the wall is complete, believing they are screwing in to a stud, when they are really screwing in to a stud + a circuit in EMT. Is that not physical damage?
(D) Cables and Raceways Parallel to Framing Members and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (1 1 ⁄ 4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm ( 1 ⁄ 16 in.) thick.
Exception No. 1: Steel plates, sleeves, or the equivalent shall not be required to protect rigid metal conduit, intermediate metal conduit, rigid nonmetallic conduit, or electrical metallic tubing.
Is it permissible to run EMT vertically on the inside channel of a metal stud?
It looks like the two requirements together (requirement and exception) boil down to:Not according to the NEC. It specifically states that EMT does not need to be set back 1.25" from the edge of the stud.
And you would be 100% wrong about that.# ~ #
Because of the "distance to the edges" issue, I would say that No,
...EMT is not permitted to be installed within metal studs......I
would cite Article 358.12, # 1 [ `08 NEC ] -
# ~ #
It looks like the two requirements together (requirement and exception) boil down to:
If you are running EMT and you can maintain the 1.25" separation you must, but if you cannot, no problem.
![]()
Look at the sentence structure again.That's not the way I read it.![]()
The code says if I want to install MC cable closer than 1 1/4 from the face of a stud I have to protect it with a 1/16th piece of metal, so I can put my MC inside of a piece of EMT or I can skip the MC just use EMT and individual conductors. Either way I'm not afraid.
# ~ #
Because of the "distance to the edges" issue, I would say that No,
...EMT is not permitted to be installed within metal studs......I
would cite Article 358.12, # 1 [ `08 NEC ] -" ...subject to severe
physical damage "........Those sheetrock screws and other types
of screws are a real detriment to the integrity of the EMT.
# ~ #