Vertical support of schedule 40 pvc

Status
Not open for further replies.
sparky....352.20(B)

LooseNuetral....the above section states:
Conduit listed for support at spacings other than as shown in Table 352.30(B) shall be permitted to be installed in accordance with the listing.

Barring some info from the manufac., NEC rules apply.
 
I found it at Table 352.30(b). Took it as meaning horizontal only. Maybe it means both. I thought vertical support could be less. Maybe I am wrong.
 
480sparky said:
It speaks of horizontal runs through framing members.

...and a bit more...
Horizontal runs of RNC supported by openings through framing members at intervals not exceeding those in Table 352.30(B) and securely fastened within 900 mm (3 ft) of termination points shall be permitted.
 
Status
Not open for further replies.
Top