SkyWarnEngineer
Member
- Location
- Texas
I just joined the forum to solicit feedback on a problem I have never before experienced. It?s a bit long so please stay with me. I have a 2.5MVA transformer that is 7.2kV primary Y and a 480V delta secondary. Our secondary uses a high resistance grounding system that consists of three small 2kVa transformers and a series of lights and a relay to indicate when we have a ground. This way we can ground any one phase and not stop any equipment (pumps) from running. An electrician walked into a block house (building with MCCs) and noticed a strange smell. He found the ?B? phase 2kVa transformer of one of our grounding systems deformed with resin running out of the case and down the wall it was mounted on. Upon investigating he found the ?B? phase fuse of the grounding system blown. He threw the disconnect switch to the ground system and checked voltage of the buss work. He found approx. 480V phase-to-phase, 410V A & C phase to earth ground, and 750V B phase to ground. His current measurements indicated no more than 3% imbalance between the phases, each were around 1500A. At this point he contacts the area electrical engineer who then contacts the rest of us to get the entire plant team together to help figure out what to do. We decide to use our 480V tie system to switch to a spare transformer, expecting the issue to be something with the transformer. We decide because of the wonky voltages to not tie the two transformers together and to get with operations and plan a brief minute or two power outage while we executed the switching order. The night before the transformer swap, operations was shedding unnecessary load. When we convened the morning of the switch we found voltages had become more normal. We measured 480V phase-to-phase and around 277V phase-to-ground for each phase. We decided to make the swap, but tie the transformers together so operations did not suffer any interruption. The swap goes flawlessly. We isolate the suspected sick transformer and call for a Doble test set and an emergency SD Myers DGA. We got with operations and got a list of all equipment that had been shed the night before the transformer swap. We then went and while measuring voltages switched everything back on and off. We found that a sump pump station, when started, gave us the same wonky voltages on the spare transformer. We were able to get consistent repeatable results turning the sump on and off. We called for a Baker test (megohm, high pot, PI, DA, etc.) test of the motor from the starter so we could verify the cable and motor. Everything passed. Somehow, a motor that runs fine, and passed all of the standard motor tests, when started, elevates phase to earth ground voltages up to 420V on ?A? and ?C? phases, and 720V on ?B? phase without effecting the current balance on the transformer, or the phase-to-phase voltage. We are at a complete loss to explain what is going on. Anyone seen anything like this before?