We recently used a 15' length of 12/3 Romex to connect two circuits in a residential garage. One circuit was dedicated to a new phone system and the second was to be used as a GFCI utility circuit. In the course of making the final connections, we noticed that we had voltage on one of the legs whose breaker at the main panel was turned off. We decided to measure the voltage and found that we had about 24 volts to either neutral or ground with the breaker turned off and the other leg powered. The bare ground and neutral were connected to the appropriate bars in the main panel. At first we suspected an induced voltage, but could not find any source for that. We disconnected the outboard end of the circuit and found the same condition existed for either leg with the other legs breaker turned on. There was no path since nothing was connected and hence no load. We then thought that perhaps there was a high resistance short somewhere in the feeder and subsequently removed it and then replaced it with another piece of three wire, but the same condition resulted. We checked the utility ground to the ground rod and found both at the same potential.
There are no florescent fixtures nearby, although there are several other parallel two wire runs to other parts of the home installed near our new feeder.
We were not successful in isolating the reason for this condition and would appreciate any sage advice you could offer.
Thanks
There are no florescent fixtures nearby, although there are several other parallel two wire runs to other parts of the home installed near our new feeder.
We were not successful in isolating the reason for this condition and would appreciate any sage advice you could offer.
Thanks