Customer supplied a 1 hp 3 ph centrifugal pump for dust suppression (add oil of some sort) in a dusty process. I do not know the model #. Viking pump direct drive.
For whatever reason the 1/4 hp was deemed no longer adequate. Don?t know why.
They also wanted a VFD on the pump to reduce flow. Ok. They had a 5 hp drive I suggested they use. Never dreamt the overload would not go low enough for the 1 hp. Yes I know, READ the directions.
System ran until I got the smaller drive. Now that I can dial in the proper over load it trips. OL1. MVX 9000. Current display indicates .9 amps, FLA is supposed to be set at 1.5 but it will not stay running under 1.9. I did not put my own meter on it.
The pump is oversized and they run it at 9hz. My thought is that the pump is running to slow and actually causing the motor current to surge a bit has it tries to maintain HZ. While the current display remains steady the drive is taking the actual current into account and tripping on overload.
I am pretty sure the piping size and location of the pump are not as suggested by the installation Manual and may add to the problem.
Thoughts or suggested corrections welcome.
For whatever reason the 1/4 hp was deemed no longer adequate. Don?t know why.
They also wanted a VFD on the pump to reduce flow. Ok. They had a 5 hp drive I suggested they use. Never dreamt the overload would not go low enough for the 1 hp. Yes I know, READ the directions.
System ran until I got the smaller drive. Now that I can dial in the proper over load it trips. OL1. MVX 9000. Current display indicates .9 amps, FLA is supposed to be set at 1.5 but it will not stay running under 1.9. I did not put my own meter on it.
The pump is oversized and they run it at 9hz. My thought is that the pump is running to slow and actually causing the motor current to surge a bit has it tries to maintain HZ. While the current display remains steady the drive is taking the actual current into account and tripping on overload.
I am pretty sure the piping size and location of the pump are not as suggested by the installation Manual and may add to the problem.
Thoughts or suggested corrections welcome.