Hi all-
Troubleshooting a phase converter and 240>400v transformer.
The situation:
We have a european spec Kuka robot in our film studio that runs off of 400v 3phase power - which must be in a Wye.
We're powering the robot via a chinese made (I know, I know) VFD + transformer thats taking 1p240v and also upping it to the required 400v. The manual is of little help as it is 100% in chinese.
When installing, there was no clear place for the neutral, so the electrician we were working with did not wire it in. SHM. Short story - when hitting the emergency stop on the robot, the power had nowhere to go and fried a piece of our robot controller.
We're replacing the KPP (kuka power pack), but obviously need to wire the VFD / controller correctly this time!
See internals of the the transformer below. Line is coming in from the top (2 hots and 1 ground, no clear spot for neutral) , Load is going out on the bottom by the coils.
Leg to Leg the robot is receiving measured ~400v
Would the pink arrows drawn in potentially be the path for the neutral from the robot?
Note - clearly I am not an electrican, I have a commercial electrician coming in over the weekend, but trying to get as much info as possible in advance.
Let the flaming begin.
Troubleshooting a phase converter and 240>400v transformer.
The situation:
We have a european spec Kuka robot in our film studio that runs off of 400v 3phase power - which must be in a Wye.
We're powering the robot via a chinese made (I know, I know) VFD + transformer thats taking 1p240v and also upping it to the required 400v. The manual is of little help as it is 100% in chinese.
When installing, there was no clear place for the neutral, so the electrician we were working with did not wire it in. SHM. Short story - when hitting the emergency stop on the robot, the power had nowhere to go and fried a piece of our robot controller.
We're replacing the KPP (kuka power pack), but obviously need to wire the VFD / controller correctly this time!
See internals of the the transformer below. Line is coming in from the top (2 hots and 1 ground, no clear spot for neutral) , Load is going out on the bottom by the coils.
Leg to Leg the robot is receiving measured ~400v
Would the pink arrows drawn in potentially be the path for the neutral from the robot?
Note - clearly I am not an electrican, I have a commercial electrician coming in over the weekend, but trying to get as much info as possible in advance.
Let the flaming begin.