hi everyone,
For a motor when sizing the cable we typically use 1.5 x FLA current. For protecting the cable we then accordingly select the CB. I have a project where i am installing VFD on a 30HP motor. My calcs for normal starter are below.
30HP, FLA=40A per NEC. So, for cable sizing = 40*1.25=50A, #8AWG should work. Now the CB should protect the cable, hence 50A CB will be selected.
Now here is the concern. I now have to install a VFD for this motor and i need to select the proper breaker. SHOULD THE 50A BREAKER ABOVE WORK FOR THE VFD?
I was also looking at the NEC. Section 430.128 states "disconnecting Means. The disconnecting means shall be permitted to be in the incoming line to the conversion equipment and shall have a rating not less than 115 percent of the rated input current of the conversion unit."
I am using ABB VFD with input current of 52A. So as per above criteria, 52*1.15=60A. IS 60A BREAKER THE RIGHT SIZE?
I am caught up between 50A & 60A breaker. I would like to know which one should i select. Any suggestions?
Thank You
Thank You