Apologies if this has already been addressed elsewhere...
I've seen multiple threads and white papers that indicate VFD cable in steel conduits is for the most part, redundant. What about VFD cable in concrete encased duct bank with PVC conduit (2" spacing between conduits)? Typically these cable runs end up being some of the longest onsite, so the added cost of VFD cable vs. vs. standard cable adds up real quick. Am I overbuilding if I put VFD cable in these underground concrete duct banks?
Additional info... (1) Our specs call for XHHW or XHHW-2 cable in all outdoor areas including below grade. (2) Other than a pair of small conductors for disabling the VFD if the local disconnect is opened, this is the only circuit in the conduit.
I've seen multiple threads and white papers that indicate VFD cable in steel conduits is for the most part, redundant. What about VFD cable in concrete encased duct bank with PVC conduit (2" spacing between conduits)? Typically these cable runs end up being some of the longest onsite, so the added cost of VFD cable vs. vs. standard cable adds up real quick. Am I overbuilding if I put VFD cable in these underground concrete duct banks?
Additional info... (1) Our specs call for XHHW or XHHW-2 cable in all outdoor areas including below grade. (2) Other than a pair of small conductors for disabling the VFD if the local disconnect is opened, this is the only circuit in the conduit.