I have a client who is relocating a 150HP VFD further away from the pump that it serves. The existing VFD cable is 3/C #4/0 with three symmetrical grounds, 2000V shieleded tray cable. I'm wondering whether we should splice the VFD cable or pull new. I've spoken to the VFD cable manufacturers and their recommendation, of course, is to provide new cable. Do any of you have experience splicing VFD cable and any input?
well, it's 600volt cable, so if you can get the same cable, it should be fairly
straightforward.... hipress butt splices for the power leads, stagger them so
they are not all at the same point, cold shrink with 3m cold shrink, do the same
with the grounds, and then wrap half lap the whole thing with copper shielding
foil, making sure the shield is maintained. i'm assuming the existing shield is a
copper foil product, not metallized mylar or something like that. after i got it
all wrapped, get someone who knows how to solder well to solder the patch
foil to the existing foil, without harming the material underneath.
then cover the whole thing with 3m cold shrink. i'm partial to 3m cold shrink
'cause it's a proven product, used in MV cable splicing kits. it's thick, it's
moisture tight, it pulls down tight, and seals.
megger and check everything for continuity with a good ohmmeter. smile,
and light it up.
how much cable is involved here? if this is a short run, it may not be worth it,
but if it's running over the river and thru the woods in a cable tray, it'd be
worth doing it.
pick someone you've got with good hand skills to do it... if anyone near you
is a cable splicer, that'll do nicely.