Is there an advantage to using VFD cable over copper conductors in conduit for short 20-30' lengths to motors?
You would be a glutten for punishment then. That's a big no-no.What about when you have the line and the load (VFD output) in the same conduit?
Exactly but isn't that one reason why you would a shielded VFD cable from the drive to the motor?You would be a glutten for punishment then. That's a big no-no.
Exactly but isn't that one reason why you would a shielded VFD cable from the drive to the motor?
I have been specifying XHHW for VFDs and for any underground conductors. There have been reports of issues with THHN/THWN and the all of the drive cable I have seen has XHHW conductors.Would you recommend XHHW-2 over THHN/W? I have seen many cases of THHN/W failing when it gets wet, esp in corrosive enviroments
both are 600 V conductors. I thought VFD cables were 1000 V conductors.I have been specifying XHHW for VFDs and for any underground conductors. There have been reports of issues with THHN/THWN and the all of the drive cable I have seen has XHHW conductors.
We just used SWAPVC.Most VFD manuals will call for shielded cable because basically everywhere else in the world, they DON'T use steel conduit, they use what we would consider something like MC cable or tray cable that is run without conduit at all and goes into cabinets via "glands". For them, it's a requirement.
In the US XHHW is most often marked as 600 volt, however the exact same wire, other than the markings is marked at 1000 volt in other countries. I expect with the code language changes in the past couple of cycles from "600 volts or less" to "1000 volts or less" we will start seeing the 1000 volt marking here.both are 600 V conductors. I thought VFD cables were 1000 V conductors.
Would you recommend XHHW-2 over THHN/W? I have seen many cases of THHN/W failing when it gets wet, esp in corrosive enviroments