Can anybody explain me in laymen terms, why a special cable is required from the output of the VFD to the motor? What happens if I don't apply a special cable? From my reading from web, I find that if I don't apply a special cable, Motor insulation damage occurs from high voltage. I do not know how the high voltage occurs. On further google search I find the terms dv/dt, high frequency, reflected wave etc. which are beyond me
It’s utter nonsense.
As far as reflected waves:
Google transmission lines.
So if you launch a pulse down a cable at the end where the motor sits the impedance is very different. It’s a big inductor compared to the cable.
Physically it’s like making a wave in a pool with a big section and a narrow section. When the wave travels down either one when it hits the change some of the wave goes through but some bounces off the edges and returns in the opposite direction.
The ratio can vary but at the joint we have the incoming pulse, tge outgoing pulse, and the reflected pulse. If the two sections are identical then it just moves like nothing happened so no reflection. Worst case nearly all of the pulse is reflected. In this case we get up to twice the pulse height or voltage. So since the pulse is equal to the DC bus which is 145% of the AC RMS input it can be around 1400 V. At around 200-250 feet this is where it is for most VFDs.
Now the wave returns to the VFD, bounces back again, bouncing back and forth until it settles out. This causes a ringing pattern. BUT if the cable is long enough then a second pulse can occur before the first one dies down. So now we can get up to 4x the DC bus.
Now 600 V cable is tested per ICEA at 200% plus 1 kV or 2200 V. NEMA did a bunch of testing. The thinnest cable, #14 THHN, fails at 2850+ V. Now the highest rated motors fail at around 1750 V. So by the time you have cable failures you will have motor failures. So what is the benefit? Higher margins for the manufacturer.
EMC:
It is very true that VFDs can emit lots of RF noise and even interfere with controls. So be careful to use shielded signals. Ir put the cable in metallic conduit.
Bearing fluting:
This is two fold. The first is that all motors have bearing currents. If the cabling is say 3 phases and a ground in a cable tray in that order as power travels down the cable you can create a condition where the voltages are unbalanced because the capacitance between the cables and ground is different. This can create circulating bearing currents but in general although the problem is dubious at best, any typical install (MC, multi conductor test cable, XHHW ir THHN in conduit with a ground) has no issues.
Second is VFDs cause common mode currents by nature. These can cause non circulating so-called “EDM currents” in bearings as well as circulating currents both of which can lead to rapid bearing destruction.
As far as “shielding” running it in metallic conduit will do, Ir bundling or using multi conductor tray cable, or using MC all do exactly the same thing. Just make sure to run a ground.
There are various other bogus claims.