I if you on a same 3 phase cable connect 5-10 3 phase VFD were they are working intermittent. How should we calaculate the cable and fuse ?
 
You've given very limited info, but I would calculate as a multiple motor feeder. 125% of the LARGEST motor, and 100% of all remaining motors.per 430.24
also meet requirements of 430.2
but if you talk to your inspector 430. 26 leaves room for debate.
 
You've given very limited info, but I would calculate as a multiple motor feeder. 125% of the LARGEST motor, and 100% of all remaining motors.per 430.24
also meet requirements of 430.2
but if you talk to your inspector 430. 26 leaves room for debate.

Yes thats what i thought
but some in this forum wants to calculate for each VFD input current.
 
Yes thats what i thought
but some in this forum wants to calculate for each VFD input current.

Almost all of the participants on this forum are experts :roll: on the NEC and would back your effort in correctly sizing this circuit. I believe the only opposition you would get is from your inspector.
 
The code does require that the feeder to the VFDs be calculated based on the VFD rated input current.
430.122 Conductors — Minimum Size and Ampacity.
(A) Branch/Feeder Circuit Conductors. Circuit conductors supplying power conversion equipment included as part of an adjustable-speed drive system shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment.
 