I if you on a same 3 phase cable connect 5-10 3 phase VFD were they are working intermittent. How should we calaculate the cable and fuse ?
You've given very limited info, but I would calculate as a multiple motor feeder. 125% of the LARGEST motor, and 100% of all remaining motors.per 430.24
also meet requirements of 430.2
but if you talk to your inspector 430. 26 leaves room for debate.
Yes thats what i thought
but some in this forum wants to calculate for each VFD input current.
430.122 Conductors — Minimum Size and Ampacity.
(A) Branch/Feeder Circuit Conductors. Circuit conductors supplying power conversion equipment included as part of an adjustable-speed drive system shall have an ampacity not less than 125 percent of the rated input to the power conversion equipment.