It's in the name more or less.
VFD stands for Variable Frequency Drive.
As AC motors for the US are generally designed around a 60 cycle supply raising or lowering the frequency of the supply will raise or lower the RPM of the motor.
It is my understanding that the changing of the frequency is the major factor at work here but the voltage is also manipulated as well to keep the motor from overheating.
By controlling the voltage the VFD can control the current. The current will have a major impact on start up torque.
Most (if not all) VFDs can also serve as motor overload protection.
Many can also be rigged with optional 'dynamic braking' which means they can make the motor work like a generator by applying a load to the circuit. This can slow motors with high inertia quite quickly without burning up mechanical braking devices. Sort of a 'Jake Brake' for electric motors if you familiar with diesel engines.
I have also read that some VFDs can be supplied with single phase but produce a 3 phase output, I have not seen this done.
Something to keep in mind is that the circuit supplying a VFD must be sized to the VFD not the motor it is controlling. NEC 430.2
Use a 25 HP rated VFD for a 5 HP motor and the supply will have to be based on 25 HP.
I have worked with VFDs from 5 to 500 HP and am always impressed with what they can do.
The 500 HP VFDs I worked with where driving 500 HP fan motors, they where programed to ramp the fans up from 0 RPM to 1740 RPM in about 7 minutes. Done this way there is absolutely no start up spike of current. If you watch the ammeter when you hit start it would go to about 50 amps immediately and than slowly ramp up to about 450 amps.
If you tried to do an full line voltage start with these motors the amperage would probably be in the 2000 to 3000 amp range. :shock:
I can tell you with certainty that the local power company was not impressed with an across the line start during commissioning. :wink:
A very common use of VFDs that I see is for the control of building HVAC fans and pumps the fans and pumps will only be spun as fast as needed to produce the needed flow at any given time to reduce energy waste.