kkp,
I believe this is correct, perhaps another member will check this post. Because there is a bypass, "across the line", starter in the VFD, I believe the calculations should simply ignore the VFD presence.
50hp = 65amps@460vac per table (art 430)
65amps x 115% = min 75amps or 50hp rated motor disconnect
(Note that this motor disconnect may not be required provided the main VFD / controller disconnecting means is lockable and otherwise suitable as the motor disconnect)
Conductor size is dependent on temperature and wiring method. (art 310)
example: 65amps x 125%(continuous load) = 81.25amps = # 4's @ 75 C
Breaker sizing (inverse time) 250% x FLA (65amps) = 162.5amps = 175amp(next std size) (art 240) Notes: breaker must be sized for motor starting "across the line" with VFD in bypass mode; breaker could be sized as large as 400% (300amp,next std size) if necessary due to motor starting current.
Len