mayanees
Senior Member
- Location
- Westminster, MD
- Occupation
- Electrical Engineer and Master Electrician
430.102(A) requires a disconnect switch for the VFD (controller). I am of the opinion that if the VFD has an integral disconnect, then that meets the NEC requirement. Our client states that their people can't work on the controller when it's energized, even if the switch is integral to the controller. I've attached a cut sheet of the 30 hP controller.
The breaker that feeds the VFD is not within sight. The installation is 480 Volt.
I understand that the facility's safety rules take precedence over the NEC, but isn't the installation NEC-compliant without a local disconnect switch?
The breaker that feeds the VFD is not within sight. The installation is 480 Volt.
I understand that the facility's safety rules take precedence over the NEC, but isn't the installation NEC-compliant without a local disconnect switch?